A transmission line rated at 1000 MVA is currently at 0 MW and 1001 Mvar. Is the line overloaded?

Prepare for the NERC EPRI Test with targeted quizzes. Explore questions with detailed hints and explanations. Ready yourself for the test!

In this scenario, the transmission line is rated for 1000 MVA, which represents its maximum apparent power capacity, combining real power (MW) and reactive power (Mvar). The current operational state of the line shows it is at 0 MW (indicating no real power flow) and 1001 Mvar (indicating solely reactive power).

To determine if the line is overloaded, it is essential to consider the concept of apparent power, which is the vector sum of real power and reactive power. The calculation involves using the formula:

( S = \sqrt{P^2 + Q^2} )

In this case, with P being 0 MW and Q being 1001 Mvar, the apparent power (S) equals:

( S = \sqrt{0^2 + 1001^2} = 1001 , MVA )

Since the apparent power of 1001 MVA exceeds the line's rated capacity of 1000 MVA, the line is indeed overloaded. This means that while there may be no real power flowing, the reactive power demand is so high that it exceeds the line's maximum rating, potentially leading to problems like voltage instability or equipment damage if sustained.

Thus